20-amp vs 15-amp home wiring

Thanks to a really wet summer last year, I get to rebuild my basement (bassment). As such, I have the opportunity to rewire everything. I have two large spools of 12g and 14g electrical wire, so is there any reason not to just redo everything with 12g and use 20-amp breakers instead of 14g/15a? I figure that with all the electronics I'm driving (some higher amps than others), it couldn't hurt. Thoughts?

15Ax120V=1800Wx80%=1440W
20Ax120V=2400Wx80%=1920W
nathanddrews is offline  
Sponsored Links
Advertisement
 
post #2 of 44 Old 04-24-2015, 06:08 AM
AVS Special Member
 
DonH50's Avatar
 
Join Date: Feb 2010
Location: Monument CO
Posts: 6,854
Mentioned: 2 Post(s)
Tagged: 0 Thread(s)
Quoted: 505 Post(s)
Liked: 406
Nope, I'd do it. Although you might save the 20 A for key circuits (bedroom probably does not need it, media room yes). Depending on your codes there may be an issue about service capacity if you run 20 A everywhere. In our area 14 AWG is used for 15 A, 12 AWG for 20 A circuits. Note 20 A circuits use a different outlet but it is compatible with standard wall plugs.
oneeyeblind likes this.

"After silence, that which best expresses the inexpressible, is music" - Aldous Huxley
DonH50 is online now  
post #3 of 44 Old 04-24-2015, 06:38 AM - Thread Starter
Advanced Member
 
nathanddrews's Avatar
 
Join Date: Jun 2012
Location: Minnesota
Posts: 992
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 64 Post(s)
Liked: 87
Quote:
Originally Posted by DonH50 View Post
Nope, I'd do it. Although you might save the 20 A for key circuits (bedroom probably does not need it, media room yes). Depending on your codes there may be an issue about service capacity if you run 20 A everywhere. In our area 14 AWG is used for 15 A, 12 AWG for 20 A circuits. Note 20 A circuits use a different outlet but it is compatible with standard wall plugs.
Right. I wasn't able to find any issues with city/state code, but I figured since some of these speakers hit over 2000W peak (on paper), it couldn't hurt anything to overbuild - other than my wallet.
nathanddrews is offline  
post #4 of 44 Old 04-24-2015, 06:51 AM
Member
 
Steve Young's Avatar
 
Join Date: Mar 2002
Location: Ontario, Canada
Posts: 114
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 1 Post(s)
Liked: 12
I would definitely do it. I recently moved into a new house (22yrs old) and I have 2 SVS PB13U subs and when the volume goes up the lights start dimming to the beat. I'm an electrician and if I could I would run 20 amp circuits everywhere in possible media room areas anyway.
oneeyeblind likes this.

Steve Young is offline  
post #5 of 44 Old 04-24-2015, 06:57 AM
AVS Special Member
 
DonH50's Avatar
 
Join Date: Feb 2010
Location: Monument CO
Posts: 6,854
Mentioned: 2 Post(s)
Tagged: 0 Thread(s)
Quoted: 505 Post(s)
Liked: 406
Check the service (breaker box) rating. If you put five 20 A breakers into a 100 A service box you are at capacity. It is fairly common to have a lot more than the service rating in breakers but that is one thing I would double-check.

When we finished our basement I had three 20 A lines run to the media plus one more to the exercise/storage room for our treadmill/clothes hanger/box holder. Everything else is standard 15 A lines.
oneeyeblind likes this.

"After silence, that which best expresses the inexpressible, is music" - Aldous Huxley
DonH50 is online now  
post #6 of 44 Old 04-24-2015, 08:50 AM
AVS Addicted Member
 
Bill Fitzmaurice's Avatar
 
Join Date: Nov 2009
Location: New Hampshire
Posts: 11,061
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 1 Post(s)
Liked: 2029
Quote:
Originally Posted by DonH50 View Post
Check the service (breaker box) rating. If you put five 20 A breakers into a 100 A service box you are at capacity. t is fairly common to have a lot more than the service rating in breakers but that is one thing I would double-check.
The number of breakers doesn't matter, the assumption being you'll not run all of them at capacity at the same time.
FWIW standard practice for decades has been to wire outlet circuits at 20a, using 15a only for lighting circuits. High draw areas, like kitchens, usually get at least two separate 20a lines.
oneeyeblind likes this.

Bill Fitzmaurice Loudspeaker Design

The Laws of Physics aren't swayed by opinion.
Bill Fitzmaurice is online now  
post #7 of 44 Old 04-24-2015, 02:17 PM
AVS Special Member
 
DonH50's Avatar
 
Join Date: Feb 2010
Location: Monument CO
Posts: 6,854
Mentioned: 2 Post(s)
Tagged: 0 Thread(s)
Quoted: 505 Post(s)
Liked: 406
Quote:
The number of breakers doesn't matter, the assumption being you'll not run all of them at capacity at the same time.
That's what I thought but apparently there's a limit in some areas. I live in the county and it didn't matter, but our electrician said it did matter in some areas (towns? I didn't ask...) I was discussing adding a transfer switch at the time since we lose power fairly often (several times a year, sometimes for an hour, sometimes a day) and asked abut service ratings. I do not recall the limit, seems like it was pretty big, like 250 % or more of the total service rating. It was five-plus years ago so my memory is a little foggy.

Quote:
FWIW standard practice for decades has been to wire outlet circuits at 20a, using 15a only for lighting circuits. High draw areas, like kitchens, usually get at least two separate 20a lines.
All the wiring I have seen in recent years (out here and in MO, only places I've been where I've dealt with it anytime recently) uses 14 AWG for standard outlets and supposedly that is only good for 15 A outlets. When I asked for 20 A they upgraded to 12 AWG and warned me at the time I would pay extra for the 20 A runs. AFAIK 14 AWG will support 20 A runs in a house (i.e. not transmission lines, just inside the house). Decades ago when I was a Journeyman 12 AWG was used everywhere for residential (except stove/range/dryer/HVAC high-current stuff). I was told the major reason for the change to 14 AWG was copper cost. The 20 A outlet is different, adds a side slot, but works with regular 15 A plugs. 30 A is a different plug (usually).

I am sure it varies from place to place and I have not looked at the actual national (NEC) regs for ages.

"After silence, that which best expresses the inexpressible, is music" - Aldous Huxley
DonH50 is online now  
post #8 of 44 Old 04-24-2015, 03:03 PM
AVS Special Member
 
BassThatHz's Avatar
 
Join Date: Apr 2008
Location: Northern Okan range (NW Cascades region)
Posts: 4,296
Mentioned: 14 Post(s)
Tagged: 0 Thread(s)
Quoted: 794 Post(s)
Liked: 680
Quote:
Originally Posted by nathanddrews View Post
I figured since some of these speakers hit over 2000W peak (on paper), it couldn't hurt anything to overbuild - other than my wallet.
Even on the 15a circuits I'd put 12awg (if you wanna). Consider it future-proofing.

Quote:
Originally Posted by Steve Young View Post
I have 2 SVS PB13U subs and when the volume goes up the lights start dimming to the beat. I'm an electrician and if I could I would run 20 amp circuits everywhere in possible media room areas anyway.
I have dual 2awg and have the same problem, when the amplifiers pull 43kW through the wire, the lights dim. In fact I might be browning out the whole hood... hehe
BassThatHz is online now  
post #9 of 44 Old 04-24-2015, 03:53 PM
Senior Member
 
eng-399's Avatar
 
Join Date: Sep 2013
Location: Plainfield il
Posts: 423
Mentioned: 4 Post(s)
Tagged: 0 Thread(s)
Quoted: 106 Post(s)
Liked: 79
My basement layout.
1- 20amp circuit for the bar area
1 -15 amp circuit for the bathroom
1-15amp for lights main area in basement
1-15 amp for outlets main basement area
2-20 amp circuits for HT room rack
1-15 amp circuit for the HT rack
1-15 amp circuit for HT room lights
1-15 amp circuit for HT outlets

I have a 200 amp breaker that I went off of and I don't see any problems with that lights which are going to be led or cfl and not everything will be running all at the same time and if there were a breaker would trip. just my 2 cents on this.

http://www.avsforum.com/forum/155-di...oot-boxes.html
The STONE HAMMERS sub box build 4/20 cubic boxes tuned @ 16hz.
http://www.avsforum.com/forum/155-di...land-area.html
2015 GTG meet Plainfield IL. (Chicago land area)
eng-399 is online now  
post #10 of 44 Old 04-24-2015, 08:46 PM
Senior Member
 
Peterc613's Avatar
 
Join Date: Apr 2011
Location: Van Nuys, CA
Posts: 352
Mentioned: 4 Post(s)
Tagged: 0 Thread(s)
Quoted: 93 Post(s)
Liked: 97
MAIN SERVICE PANNEL

If you add up all the breakers in your main service panel, it is normal for the total to exceed the rated capacity of the box. That is because it's assumed that you will not be using all circuits at their full capacity at the same time. When the house is built, a load calculation is done on all the appliances, AC, outlets and lighting loads that might be in use at the same time to determine the size the main panel.

WIRE

The breaker size and wire gauge for each circuit are determined by the type of load. The rule of thumb is that nominal load should not exceed 80% of capacity. Therefore, for convenience outlets you typically run 12 awg wire capable of 20 amps even if the breaker and receptacles are rated at only 15 amps. It's not uncommon to run 12 awg wire to a switch box with multiple 300w/600w dimmers then run 14 awg on the switch leg from each dimmer to the lighting loads.

THNN solid core wire will carry a greater maximum amperage than stranded wire. It's always easier to run 12 awg wire and limit the circuit to 15 amps with the breaker and receptacle, than to decide later you want 20 amps and re-pull wire through a crowded conduit or Romex through walls under sealed drywall. Your time and labor are much more expensive than the cost difference between 12 and 14 AWG.

BREAKERS

Think of electricity like water. It comes in from the street on two hot wires (phase one & phase two) and then returns to the source through one common wire. The local utility sends a 110v pulse on phase one, then a 110v pulse on phase two, then back to 110v on phase one, and so on. In your Main service panel there are two sets of copper rails for phase one and phase two. A 110v "single-pole" breaker will snap onto only one rail, a 220v "double-pole" breaker will snap onto both rails.

Breakers come in different configurations: (1) Half size 1/2" single pole , (2) Full size 1" single pole or double pole (3) Twin 1" two single pole, and (4) Quad size 2" four single, two double pole or a combination thereof. When you add a circuit, you simply pull out one or more Full size breakers and replace them with Twins or Quads to free up one or more unoccupied terminals.

PHASE

Phase is important to keep track of because typically you will run three wires (two hots and a common) from the main panel to a given location. Each hot wire is on a different phase and they share the common wire with the current alternating between them. if you get your commons mixed up at the end location, you can have two hots trying to drain through the same common and overheat the common wire. You can also get voltage feeding back through dimmers or an adjacent load if you don't keep track of which common goes to which load.

Typically electricians run black for phase one, red for phase two, and white for the common to keep track of phases at the end location, using colored wires to differentiate switch legs or branch circuits. Typically, I will run all my hots and commons in red, black and white to a junction box in the Theater area, then make it up with colored wire pulled to the various receptacles.

AUDIO

For audio equipment, especially power hungry amplifiers, I always run 12 awg, with 20 amp breakers and 20 amp receptacles. There are expensive audiophile receptacles from PS Audio and others, but a standard hospital grade outlet from your local electrical supply is more than comparable.

When running multiple amplifiers in home theater, it's important to do a load calculation and distribute the amplifiers over a sufficient number of circuits. You can get the maximum current draw of each amplifier from the specifications in the owners manual or by calling the manufacturer's technical support. Remember that the rule of thumb is 80% load to capacity. A receptacle wired for 20a/110v is rated for 2200va, so two amplifiers rated at 850va each will just about use up one 20 amp circuit.

Many high power multichannel amplifiers can easily take up a 20 amp circuit on their own. Multiple subs in an installation can also require one or more circuits (although the newer class D amps may use less power than a traditional class a/b amp). If possible, keep the electronics and video on a separate circuit so that they are not effected by a surge in demand from multiple amplifiers during demanding special effects.

GROUND LOOPS

Ground loops occur whenever the grounding potential one receptacle location is significantly stronger than another. They can be difficult to track down and aggravating to eliminate. To preempt ground loops when I pull wire for a theater, I usually pull a 12 awg green ground wire along with my hots and commons (or the bare copper ground wire in Romex) from the receptacles in the theater room to the Theater central junction box. From there I wire nut them to a 10 awg stranded green wire back to the ground block in the main panel. Most main panels have a heavy gauge wire connecting their grounding block directly to a nearby long copper rod hammered deep into the ground. This guarantees that the grounding potential for all receptacles is greatest at one common point at the theater junction box.
Skytrooper likes this.
Peterc613 is online now  
post #11 of 44 Old 04-24-2015, 11:06 PM
Senior Member
 
Peterc613's Avatar
 
Join Date: Apr 2011
Location: Van Nuys, CA
Posts: 352
Mentioned: 4 Post(s)
Tagged: 0 Thread(s)
Quoted: 93 Post(s)
Liked: 97
DWP had two 100 amp drops to our house, one for the main panel and one for the 30 amp AC. After doing a load calculation I installed a new main panel on the second 100 amp drop and ran about 50 feet of 2" conduit to a sub-panel in the AV closet. Then I pulled 3 dedicated 20A/120V circuits using 10 awg stranded wire for three subs, 4 dedicated 20A/120V circuits using 12 awg THNN wire for eight amps, 2 dedicated 20A/120V circuits using 12 awg THNN wire for audio and video electronics, and one 20A/120V circuit using 12 awg THNN wire for regular wall outlets and to power 12 Martin Logan Electrostatic speakers.

Our theater is part of a 1,200 sq ft open floor plan with 5 dedicated 20A/120V circuits using 12 awg THNN wire for 5 Lutron Graphic Eye 6-zone dimmers for recessed halogen lighting. All of the electrical outlets in the theater have isolated grounds home run with 12 awg THNN to the sub-panel, then back to the main panel with 10 awg stranded to eliminate ground loops.

I took a class at CEDIA one year from the head designer at Fuhrman who recommended keeping all a/v branch circuits on the same phase. So every hot wire for the amps, subs, electronics and video has its own dedicated common wire so that all breakers for the theater can be on the same phase at the main panel.
Peterc613 is online now  
post #12 of 44 Old 04-25-2015, 07:34 AM
Advanced Member
 
Red99's Avatar
 
Join Date: Sep 2014
Location: Pacific Northwest
Posts: 635
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 362 Post(s)
Liked: 158
Hey thanks for the electrical 101. I am about to run a couple dedicated lines to my family room for the new subs I have on order. Right now everything (64" plasma TV, My Amp and Pre-amp, BR, and all lights are coming from a single 15a breaker. I put a plug in amp load tester and I am only drawing about 6 amps the most. But the subs I am getting has 2400w amps each, so I think that will be pushing it. And I want to bridge my McIntosh amp latter and use it for the LCR channels that will be 320w per channel and get a 2nd amp for the surrounds and may some heights. I was told the sub amps are very efficient and would probably run just fine on 15 amp. But I am not sure with everything else. I could also run the amps on 230V, but I was told there is no real advantage as long as there is no voltage drop. And I think that is an important thing to think about when running wire. The longer the wire, the more of a voltage drop right? I even thought about running a 10/3 wire, just in case I ever wanted to go to 230V then the wire would be there and just not use the one leg for 110v. But I will have to run this from my garage to my family room in a pre-built house, so trying to fish 10g wire might be a bit of a headache. Im just trying to decide if I want to tackle this myself or hire an electrician.
Also, my breaker box has about 330 amps of breakers in it now and they are all full. So I guess I would have to use one of those tandem breakers to free up some slots. I have no idea what my main breaker is! There is no making on it. The box I believe is a 20-20. So I don't know if I need to upgrade the box or not. A lot of unknowns. Would a electrician want to hook up the wires at the box and check or hook up the receptacle if I run the wire and do all the labor intensive work? Or would he be worried of a liability issue?


SOUND: Marantz AV-7702 Pre/Pro, McIntosh MC1706 Amp,
(2) Klipsch RF7-II's, (2) Funk Audio 18.0 subs

VIDEO:
Samsung PN64F8500 Plasma TV, Oppo 103D Blue Ray Player
Red99 is offline  
post #13 of 44 Old 05-06-2015, 05:42 AM
Advanced Member
 
Red99's Avatar
 
Join Date: Sep 2014
Location: Pacific Northwest
Posts: 635
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 362 Post(s)
Liked: 158
I got a question. I had 2 electricians come out and give me a estimate on finishing my twin 20A circuits I am installing for the Home Theater System. One of them is bypassing the permit and just using standard 20 amp breeakers. The other will only do it with a permit, and says I will have to use AFCI breakers. I read some reviews of people having trouble with Arc Fault breakers tripping too easy. But so far its been either a Microwave or vacuum cleaner. Has anyone used the AFCI breakers for the high powered amps? And if so, any problems?


SOUND: Marantz AV-7702 Pre/Pro, McIntosh MC1706 Amp,
(2) Klipsch RF7-II's, (2) Funk Audio 18.0 subs

VIDEO:
Samsung PN64F8500 Plasma TV, Oppo 103D Blue Ray Player
Red99 is offline  
post #14 of 44 Old 05-06-2015, 06:41 AM
AVS Addicted Member
 
Bill Fitzmaurice's Avatar
 
Join Date: Nov 2009
Location: New Hampshire
Posts: 11,061
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 1 Post(s)
Liked: 2029
AFCI protection, via either the breaker or outlet, is required as of 2014 by the NEC. However, the NEC isn't locally binding. Local standards are set by individual states and municipalities. They may adopt NEC standards, but they may not. When in doubt as to what you must have check with your local code enforcement officer.

Bill Fitzmaurice Loudspeaker Design

The Laws of Physics aren't swayed by opinion.
Bill Fitzmaurice is online now  
post #15 of 44 Old 05-06-2015, 08:58 AM
AVS Special Member
 
DonH50's Avatar
 
Join Date: Feb 2010
Location: Monument CO
Posts: 6,854
Mentioned: 2 Post(s)
Tagged: 0 Thread(s)
Quoted: 505 Post(s)
Liked: 406
+1. They are required in my county as of a few years ago, not in some other areas. We had problems with one flipping in our boy's bedroom when our treadmill (in a different room, on a different breaker) was cycled. Both are on a basement sub-service. The media room breakers did not trip (for 15 A outlets; dedicated 20 A outlets did not have them). Same service, might be on a different phase (not sure at this point). The offending AFCI breaker was replaced a couple of times and then I put in a regular breaker. Not code, but kept my boy from being in the dark.

At that time, in our area, they were required in certain rooms but not all (bedrooms; kitchen/bath had GFI, etc.) And, they were not required on my 20 A dedicated lines in the media room, or at least that's what the electrician told me. It passed inspection, who knows... Our county's website was very helpful, as was the inspector's office.

"After silence, that which best expresses the inexpressible, is music" - Aldous Huxley
DonH50 is online now  
post #16 of 44 Old 05-06-2015, 06:58 PM
Advanced Member
 
Red99's Avatar
 
Join Date: Sep 2014
Location: Pacific Northwest
Posts: 635
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 362 Post(s)
Liked: 158
I will just have to take the electricians word for it. I went and picked up 2 - 20A AFCI's at lunch. It seems like a good idea. I just think the technology isn't there yet. But, if I have trouble with them tripping after its inspected, then I will just replace them with a standard breaker. I will also ask the inspector when he comes out to do the inspection if I really need them for the family room.


SOUND: Marantz AV-7702 Pre/Pro, McIntosh MC1706 Amp,
(2) Klipsch RF7-II's, (2) Funk Audio 18.0 subs

VIDEO:
Samsung PN64F8500 Plasma TV, Oppo 103D Blue Ray Player
Red99 is offline  
post #17 of 44 Old 05-06-2015, 08:16 PM
Senior Member
 
Peterc613's Avatar
 
Join Date: Apr 2011
Location: Van Nuys, CA
Posts: 352
Mentioned: 4 Post(s)
Tagged: 0 Thread(s)
Quoted: 93 Post(s)
Liked: 97
Quote:
Originally Posted by Red99 View Post
Hey thanks for the electrical 101. I am about to run a couple dedicated lines to my family room for the new subs I have on order. Right now everything (64" plasma TV, My Amp and Pre-amp, BR, and all lights are coming from a single 15a breaker. I put a plug in amp load tester and I am only drawing about 6 amps the most. But the subs I am getting has 2400w amps each, so I think that will be pushing it. And I want to bridge my McIntosh amp latter and use it for the LCR channels that will be 320w per channel and get a 2nd amp for the surrounds and may some heights. I was told the sub amps are very efficient and would probably run just fine on 15 amp. But I am not sure with everything else. I could also run the amps on 230V, but I was told there is no real advantage as long as there is no voltage drop. And I think that is an important thing to think about when running wire. The longer the wire, the more of a voltage drop right? I even thought about running a 10/3 wire, just in case I ever wanted to go to 230V then the wire would be there and just not use the one leg for 110v. But I will have to run this from my garage to my family room in a pre-built house, so trying to fish 10g wire might be a bit of a headache. Im just trying to decide if I want to tackle this myself or hire an electrician.
Also, my breaker box has about 330 amps of breakers in it now and they are all full. So I guess I would have to use one of those tandem breakers to free up some slots. I have no idea what my main breaker is! There is no making on it. The box I believe is a 20-20. So I don't know if I need to upgrade the box or not. A lot of unknowns. Would a electrician want to hook up the wires at the box and check or hook up the receptacle if I run the wire and do all the labor intensive work? Or would he be worried of a liability issue?
10/3 wire is really overkill. You should be fine with 12/3 Romex.

Voltage drop on 100v is not really an issue if you plan your load to be 80% of capacity (i.e. about 1,800 watts on a 20 amp line).

I have found AFCI's to be a pain in the ass on exterior loads where dampness creates some grounding issues. They also tend to trip on variable motor loads (when the motor first starts up, it pulls a lot of amps to overcome inertia). I haven't used then for a HT so I don't have direct experience with AFCI's and power hungry amplifiers.

You can save a lot of money by running the Romex, mounting the j-boxes and terminating the outlets yourself and have the electrician terminate the wire at the main panel. It's easy, there are DIY videos on youtube and picture books at Home Depot. Just use Romex staples to secure the lines, always drill your holes through studs in the middle and leave more than enough romex at the end looped up so he's not short on routing the wire in the main panel.

Last edited by Peterc613; 05-06-2015 at 08:26 PM.
Peterc613 is online now  
post #18 of 44 Old 05-06-2015, 09:11 PM
Advanced Member
 
Red99's Avatar
 
Join Date: Sep 2014
Location: Pacific Northwest
Posts: 635
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 362 Post(s)
Liked: 158
I went with 12-2 romex (not counting the ground wire) since I decided to stick with 120V. The electrician said it had to be stapled every 4 feet. But I did it on each rafter. I had a box of them so what the heck. I just finished shoving all the wire I need to behind the outlet and have all wire in the attic stapled except about 10 feet before it drops to the service panel. I don't know if its matters, but I took the time to make the wire run nice and straight and kept the wire flat without any twist.
The Electrician is charging me $201 ($133.50 for time + $52.23 for permit + $15.60 tax) to run the wire from the attic down to the panel and install the new breakers and wire it up.

The panel says 2020, but I found out that it can us 40 circiuts ( 20 of the narrow 1/2" breakers ). GE doesn't use the tandem or duplex breakers, they use a half width breaker instead.


SOUND: Marantz AV-7702 Pre/Pro, McIntosh MC1706 Amp,
(2) Klipsch RF7-II's, (2) Funk Audio 18.0 subs

VIDEO:
Samsung PN64F8500 Plasma TV, Oppo 103D Blue Ray Player
Red99 is offline  
post #19 of 44 Old 05-08-2015, 08:12 PM
AVS Special Member
 
blazar's Avatar
 
Join Date: Oct 2004
Location: USA
Posts: 3,203
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 539 Post(s)
Liked: 420
If you want to go nuckin futs... I would add a 30 amp breaker in the media closet just in case you want to buy yourself a "mega" amp for huge subs. I have at least 5 15 amp outlets leading to my closet as well.

Additionally I have a blind ended outlet going to from my media closet to my projector area. This way I can plug in the projector into my furman balanced power conditioner where everything else is plugged in. eliminates the possibility of ground loops.

I believe no room should ever be designed without quad DIY subs with high power rack mount amps. Epic bass that is relatively cheap, hidden, easy to build.

Blazar!
blazar is online now  
post #20 of 44 Old 05-08-2015, 08:51 PM
AVS Special Member
 
PrimeTime's Avatar
 
Join Date: Mar 2003
Location: Lower California
Posts: 2,035
Mentioned: 1 Post(s)
Tagged: 0 Thread(s)
Quoted: 185 Post(s)
Liked: 81
One rule of thumb I would recommend to those running Romex: Use three-conductor Romex. This will permit two 20-amp circuits at one location, if needed. Opposite-phase circuits with (hopefully) somewhat balanced loading and reduced neutral (white wire) current and the ability for a 220-volt connection, if required.
PrimeTime is online now  
post #21 of 44 Old 05-09-2015, 01:02 PM
Senior Member
 
Peterc613's Avatar
 
Join Date: Apr 2011
Location: Van Nuys, CA
Posts: 352
Mentioned: 4 Post(s)
Tagged: 0 Thread(s)
Quoted: 93 Post(s)
Liked: 97
Quote:
Originally Posted by PrimeTime View Post
One rule of thumb I would recommend to those running Romex: Use three-conductor Romex. This will permit two 20-amp circuits at one location, if needed. Opposite-phase circuits with (hopefully) somewhat balanced loading and reduced neutral (white wire) current and the ability for a 220-volt connection, if required.
DITTO...

I almost always use 12/3 Romex whenever we're not pulling through conduit. Most of your cost is in labor and installation time. Having the spare conductor more than pays for itself in flexibility in the long run.


It's a rule of thumb that:

Just as the drywall is buttoned up, people decide to make changes.

Just as the dimmers are wired, people are going to want a three way dimmer across the room

After the project's complete and in use, you start thinking of all the things you left out.

You'll get new gear, and see what others are doing, it's human nature to want more.

Eventually you'll decide to expand, and will need the extra wire for something else.


Ponder these likely scenarios:

Another circuit for additional subwoofers, more powerful amps, more amps for height speakers (You KNOW you're going to want Atmos Auro DTS-X when it becomes the norm). How about when the time comes to extend your A/V equipment into distributed audio (more zone amps) around the house and even an outside pool-plex theater for your kids (easy to do and REALLY COOL! - just add outside speakers, HDMI baluns for a projector hook up, and an inexpensive inflatable screen).

Want to add power conditioning to reduce line noise and add dynamic range above the noise floor? Adding a dedicated circuit just for your amplifiers will do more to improve the sound than most power conditioners up to $500.

To make your theater space look really dramatic, you're going to need another circuit for additional lighting. Most people think of direct lighting when they consider interior lights. Instead think of your theater lighting as a blank canvas that you paint with different light tools and dark areas. Recessed indirect lighting on wall art, Recessed task lighting at the equipment rack, bar top, or sofa table, Up lighting behind plants or speakers to paint shadows on the walls or ceiling. The majority of the luminance in the room should come from these sources. Leave dark areas to frame the objects lit. Use table top lights for accent, and fill lights to raise the ambient light in darker areas. Some people add floods just for cleaning. All of those lighting switch legs require a separate hot wire back to the dimmer. Put all that on a Lutron Graphic Eye or multiple z-wave dimmers on a IR screen control master switch and you've easily added another 20 amp circuit.

A heater to compensate for cold in winter (especially if it's a basement HT conversion). An A/C mini-split to keep it cool in summer (especially if it's a garage or exterior room addition). Besides, by the time you heat up your theater room with several amplifiers, a hot projection lamp, and multiple bodies you may need the A/C anyway.

Or maybe you just decide to add another guest bathroom for all the people coming over to enjoy your theater. Whatever comes up, you'll be really happy that all you have to do is use the existing surplus conductor that's capped in the back of the j-box and main panel (as opposed to hiring a crew to open up all your drywall to run new lines.)
Attached Thumbnails
Click image for larger version

Name:	Unknown-3.jpeg
Views:	16
Size:	5.1 KB
ID:	708658   Click image for larger version

Name:	Grafik-eye-QS.jpg
Views:	18
Size:	10.2 KB
ID:	708666   Click image for larger version

Name:	John's Light plan_00001.jpg
Views:	20
Size:	23.8 KB
ID:	708882  

Last edited by Peterc613; 05-09-2015 at 02:31 PM.
Peterc613 is online now  
post #22 of 44 Old 05-09-2015, 05:40 PM
Advanced Member
 
Red99's Avatar
 
Join Date: Sep 2014
Location: Pacific Northwest
Posts: 635
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 362 Post(s)
Liked: 158
Quote:
Originally Posted by PrimeTime View Post
One rule of thumb I would recommend to those running Romex: Use three-conductor Romex. This will permit two 20-amp circuits at one location, if needed. Opposite-phase circuits with (hopefully) somewhat balanced loading and reduced neutral (white wire) current and the ability for a 220-volt connection, if required.
I thought it was best to have all the audio on the same phase? And would having 2 seperate 110 outlets share the same neutral back to the panel be within code? And what about having any ground loop issues doing this? I am just curious because it makes sense, but I have never seen this done.


SOUND: Marantz AV-7702 Pre/Pro, McIntosh MC1706 Amp,
(2) Klipsch RF7-II's, (2) Funk Audio 18.0 subs

VIDEO:
Samsung PN64F8500 Plasma TV, Oppo 103D Blue Ray Player
Red99 is offline  
post #23 of 44 Old 05-11-2015, 05:07 AM
AVS Special Member
 
blazar's Avatar
 
Join Date: Oct 2004
Location: USA
Posts: 3,203
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 539 Post(s)
Liked: 420
I put all the av outlets and stuff for the whole house on one phase so that i dont have future ground loops. They could still occur despite all these efforts.

So far no issues that I have experienced.
blazar is online now  
post #24 of 44 Old 05-11-2015, 07:04 AM
AVS Special Member
 
DonH50's Avatar
 
Join Date: Feb 2010
Location: Monument CO
Posts: 6,854
Mentioned: 2 Post(s)
Tagged: 0 Thread(s)
Quoted: 505 Post(s)
Liked: 406
I don't buy the ground loop issue as being a reason for keeping everything on one phase in a consumer installation. It's possible a single phase could help or hurt that situation. It certainly hurts load balancing at the service so I would tend to alternate phases.

YMMV - Don

"After silence, that which best expresses the inexpressible, is music" - Aldous Huxley
DonH50 is online now  
post #25 of 44 Old 05-11-2015, 07:19 AM
Advanced Member
 
Ted99's Avatar
 
Join Date: Jul 2004
Location: Houston, TX
Posts: 748
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 82 Post(s)
Liked: 46
One often omitted item is the outlets. Use "Hospital-grade" outlets. They are 20 amp and have tighter contacts in the sockets. If you buy them at Home Depot, they will be orange. You can get other colors and decorator style with rectangular shape at an electric supply house. I am always amused at the people that spend Hundreds/thousands of dollars for a "high end" IEC cable from the outlet to the gear, forgetting that there is 100' of romex costing pennies per foot leading to the outlet, and then a dollar outlet. Also, many times several outlets have been wired in series on a circuit. Many builders have used the "push-type" outlets for quick assembly. Take all of those off and use the side screw terminals for better current conduction. The hospital grade outlets do not have a connection between the frame of the outlet and the ground wire. If you have metal outlets and metal conduit, this avoids another possible source for ground loops.
Ted99 is offline  
post #26 of 44 Old 05-11-2015, 11:53 AM
Senior Member
 
Peterc613's Avatar
 
Join Date: Apr 2011
Location: Van Nuys, CA
Posts: 352
Mentioned: 4 Post(s)
Tagged: 0 Thread(s)
Quoted: 93 Post(s)
Liked: 97
Quote:
Originally Posted by Ted99 View Post
One often omitted item is the outlets. Use "Hospital-grade" outlets. They are 20 amp and have tighter contacts in the sockets. If you buy them at Home Depot, they will be orange. You can get other colors and decorator style with rectangular shape at an electric supply house. I am always amused at the people that spend Hundreds/thousands of dollars for a "high end" IEC cable from the outlet to the gear, forgetting that there is 100' of romex costing pennies per foot leading to the outlet, and then a dollar outlet. Also, many times several outlets have been wired in series on a circuit. Many builders have used the "push-type" outlets for quick assembly. Take all of those off and use the side screw terminals for better current conduction. The hospital grade outlets do not have a connection between the frame of the outlet and the ground wire. If you have metal outlets and metal conduit, this avoids another possible source for ground loops.

COMPLETE LIST LEVITON HOSPITAL GRADE OUTLETS:

http://communities.leviton.com/servl...%205490-IG.pdf
Peterc613 is online now  
post #27 of 44 Old 05-11-2015, 05:42 PM
Advanced Member
 
Red99's Avatar
 
Join Date: Sep 2014
Location: Pacific Northwest
Posts: 635
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 362 Post(s)
Liked: 158
OK, I am installing my outlet tonight and the electrician is coming tomorrow to finish the run from the Attic down to the service panel. I have 12-2 ROMEX. Will this work or not work for the Hospital grade outlet? I don't understand the grounding of it.
Also, I picked up a single outlet Receptacle instead of the duplex. Is this OK or bad? I can take it back for an exchange or refund. I need to finish up the outlet end tonight before the electrician comes out tomorrow.


SOUND: Marantz AV-7702 Pre/Pro, McIntosh MC1706 Amp,
(2) Klipsch RF7-II's, (2) Funk Audio 18.0 subs

VIDEO:
Samsung PN64F8500 Plasma TV, Oppo 103D Blue Ray Player
Red99 is offline  
post #28 of 44 Old 05-11-2015, 06:03 PM
Senior Member
 
Peterc613's Avatar
 
Join Date: Apr 2011
Location: Van Nuys, CA
Posts: 352
Mentioned: 4 Post(s)
Tagged: 0 Thread(s)
Quoted: 93 Post(s)
Liked: 97
Quote:
Originally Posted by Red99 View Post
OK, I am installing my outlet tonight and the electrician is coming tomorrow to finish the run from the Attic down to the service panel. I have 12-2 ROMEX. Will this work or not work for the Hospital grade outlet? I don't understand the grounding of it.
Also, I picked up a single outlet Receptacle instead of the duplex. Is this OK or bad? I can take it back for an exchange or refund. I need to finish up the outlet end tonight before the electrician comes out tomorrow.
Definitely swap the single outlet for a double. If fact if you can, Home Depot has Wire Mold dual gang surface J-boxes that would allow you to use two duplex receptacles. They screw right on top of your single gang opening. Most A/V racks have several pieces of equipment that need an outlet. Plugging each one into an outlet is better than sharing a power strip. Four outlets will power most of your gear with minimal power strips.
Attached Thumbnails
Click image for larger version

Name:	Wire Mold_00001.jpg
Views:	12
Size:	12.0 KB
ID:	711922  
Peterc613 is online now  
post #29 of 44 Old 05-11-2015, 07:01 PM
Advanced Member
 
Red99's Avatar
 
Join Date: Sep 2014
Location: Pacific Northwest
Posts: 635
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 362 Post(s)
Liked: 158
OK thanks. I was going with the two singles so it stands out as two separate dedicated 20A circuits. At first I was thinking of running each circuit to each outlet on the duplex. (Top half is one circuit, and bottom half another circuit). The electrician looked at my funny and said he could do that, but its not common practice.


SOUND: Marantz AV-7702 Pre/Pro, McIntosh MC1706 Amp,
(2) Klipsch RF7-II's, (2) Funk Audio 18.0 subs

VIDEO:
Samsung PN64F8500 Plasma TV, Oppo 103D Blue Ray Player
Red99 is offline  
post #30 of 44 Old 05-11-2015, 07:41 PM
Senior Member
 
Peterc613's Avatar
 
Join Date: Apr 2011
Location: Van Nuys, CA
Posts: 352
Mentioned: 4 Post(s)
Tagged: 0 Thread(s)
Quoted: 93 Post(s)
Liked: 97
Quote:
Originally Posted by Red99 View Post
OK thanks. I was going with the two singles so it stands out as two separate dedicated 20A circuits. At first I was thinking of running each circuit to each outlet on the duplex. (Top half is one circuit, and bottom half another circuit). The electrician looked at my funny and said he could do that, but its not common practice.
I split receptacles all the time. The top half is switched for table lamps and the bottom half is a convenience outlet. I also use a lot of up lighting in my installs for dramatic flair, so we configure split receptacles for floor up lights behind potted indoor plants.

You do know that 12/2 will not support two 20A circuits, you need 12/3 for that.

12/2 - one hot, one common, one ground

12/3 - two hots, pne common, one ground
Peterc613 is online now  
Sponsored Links
Advertisement
 
Reply Subwoofers, Bass, and Transducers

Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page


Forum Jump: 

Posting Rules  
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off