So I need to run a bunch of cable from my equipment rack to the theater... I am estimating about a 1.5" conduit. I am thinking of using smurf pipe, but here are the issues:

1) I need to cut a 1.5" hole in the header
2) The smurf pipe will basically exit into the room (no terminators)

So how does one deal with a 1.5" pipe which is a wide open "straw" into the attic? Doesn't this put a big damper on the whole isolation thing??

Any suggestions?

Thanks!
WannaTheater is offline  
Sponsored Links
Advertisement
 
post #2 of 16 Old 08-09-2010, 08:28 PM
AVS Addicted Member
 
Stereodude's Avatar
 
Join Date: Jan 2002
Location: Detroit Metro Area
Posts: 10,132
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 663 Post(s)
Liked: 632
I think the goal is to create an airtight seal around the conduit so sound can't escape that way, and make sure the conduit doesn't end somewhere you can't tolerate some noise leakage. You will also want to stuff the conduit with something to try to make it airtight on both ends as well.
Stereodude is offline  
post #3 of 16 Old 08-09-2010, 08:31 PM
AVS Special Member
 
snickel's Avatar
 
Join Date: Dec 2007
Location: South central Kansas
Posts: 1,158
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
foam it shut?
snickel is offline  
post #4 of 16 Old 08-09-2010, 09:46 PM
AVS Special Member
 
Brad Horstkotte's Avatar
 
Join Date: Dec 2005
Location: Torrance, CA
Posts: 5,125
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 12 Post(s)
Liked: 57
If the conduit runs from the equipment room, through the attic, and into the theater - then it isn't open to the attic, just on both ends. So maybe just cover the conduit running through the attic with a fiberglass blanket if sound escaping through the conduit walls into the attic is a concern. Or were you concerned with sound leaking out the end of the conduit into the equipment room?
Brad Horstkotte is online now  
post #5 of 16 Old 08-10-2010, 04:32 AM - Thread Starter
Senior Member
 
WannaTheater's Avatar
 
Join Date: Aug 2006
Location: Tampa, FL
Posts: 492
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 2 Post(s)
Liked: 10
I can go either way -

I can run conduit just up the theater wall into attic and leave it open, which will cause sound to leak into the attic

Or I can run full conduit up theater wall, across attic, and into cabinet. But my cabinet is actually in the closet of a bedroom, so I am concerned that I am providing a nice easy path for sound to travel through.
WannaTheater is offline  
post #6 of 16 Old 08-10-2010, 04:55 AM
AVS Club Gold
 
Dennis Erskine's Avatar
 
Join Date: Jul 1999
Location: Near an airport
Posts: 9,143
Mentioned: 1 Post(s)
Tagged: 0 Thread(s)
Quoted: 17 Post(s)
Liked: 47
Here's the best you can do (why am I telling people this? geeze, it takes money out of my pocket. Hey buddy, you got a buck for a cup of coffee?)

Where the conduit enters the room (through the drywall), maker certain the conduit does not touch the drywall. You can use a flexible caulk (Ted has some acoustic caulk that will work well) to seal the gap between the conduit and drywall.

Where the conduit passes through framing, cut the hole bigger than the conduit and do exactly the same thing ... don't let it touch the framing...use caulk to seal the gap.

Where the conduit runs through a wall, make certain it cannot contact either side of the walls (back side of the drywall) or any framing ... you don't want rattles. Where you use clamps or attaching brackets to secure the conduit inside the walls, get slightly oversized and use pipe wrap between the bracket and the conduit.

If you want to go "over the top", wrap the entire conduit run.

At each end, once your wires are pulled, plug the ends with fiberglass but make sure you can pull that fiberglass out in case you run a new wire in the future.

Dennis Erskine CFI, CFII, MEI
Architectural Acoustics
Subject Matter Expert
Certified Home Theater Designer
CEDIA Board of Directors
www.erskine-group.com
www.CinemaForte.net
Dennis Erskine is offline  
post #7 of 16 Old 08-10-2010, 05:24 AM
AVS Special Member
 
ctviggen's Avatar
 
Join Date: Dec 2003
Posts: 1,918
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 14 Post(s)
Liked: 19
Doesn't he have to use fire caulking if he's cutting a hole in the header? Is the acoustic caulk fire-rated?

Bob
ctviggen is offline  
post #8 of 16 Old 08-10-2010, 06:00 AM
AVS Special Member
 
Elill's Avatar
 
Join Date: Dec 2007
Location: Sydney, Australia
Posts: 1,468
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 19 Post(s)
Liked: 22
The sealants I've found that have the same flex properties are fire rated.....gtee 10+ years they stay soft and flexible....that's why they're good for these applications

Peter the Greek

Downunder Theatre MkII
Redefining snail pace construction
"what is worth knowing is difficult to learn"

Elill is offline  
post #9 of 16 Old 08-10-2010, 06:12 AM
Senior Member
 
Gelfling's Avatar
 
Join Date: Jun 2002
Location: Milford, Delaware
Posts: 335
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
Okay. I'm going to go out on a limb here. Those of you that follow my thread know that I have been very anal about my sound isolation, however, in the OP's case....I would just stuff some fiberglass in the conduit. What we are really talking about here is about 3 square inches of space out of many, many square feet of wall space. So some of the sounds leaks? Really? Into the attic? So what. Now, the only arguement from a physics standpoint I can see is that if this guy really has an air tight room, then that 3 square inches does ruin it. Howoever, I would venture to say that very, very few of us really have an air tight room.

I still can't believe what side of the fence I am find myself coming down on.
Gelfling is offline  
post #10 of 16 Old 08-10-2010, 06:26 AM
AVS Special Member
 
ctviggen's Avatar
 
Join Date: Dec 2003
Posts: 1,918
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 14 Post(s)
Liked: 19
Quote:
Originally Posted by Elill View Post

The sealants I've found that have the same flex properties are fire rated.....gtee 10+ years they stay soft and flexible....that's why they're good for these applications

This is the acoustic caulking I have:

http://www.soundproofingcompany.com/products/silenseal/

For holes through the top plate, my inspector required that I fire caulk these. I did not use the above acoustic caulking and instead used 2 hour fire rated caulking:

http://cableorganizer.com/3m-fire-pr...ier-ic15wb.htm

The fire rated caulking expands when heated. I am unsure if the acoustic caulking does this.

So, does a header need simply to be caulked or be caulked with fire rated caulking?

Bob
ctviggen is offline  
post #11 of 16 Old 08-10-2010, 09:48 AM
Member
 
etk29321's Avatar
 
Join Date: Dec 2001
Location: Cary, NC
Posts: 175
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 11
When I finished off a room this year, the inspector specifically looked for fire-rated caulk in any hole in a header. In a wall, you could use whatever you wanted, but headers were a special case. He wasn't going to pass me unless it was fire-rated. The fire-rated caulk I see in lowes here is also colored bright red.
etk29321 is offline  
post #12 of 16 Old 08-10-2010, 11:35 AM
AVS Addicted Member
 
Stereodude's Avatar
 
Join Date: Jan 2002
Location: Detroit Metro Area
Posts: 10,132
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 663 Post(s)
Liked: 632
Quote:
Originally Posted by etk29321 View Post

The fire-rated caulk I see in lowes here is also colored bright red.

Home Depot sells 4 different grades of it that are rated for slightly different uses. The cheapest, 3M FB 136, is gray and dries very hard (like plastic). It's only intended for framing gaps and not for penetrations made by cables or pipes. For penetrations they sell 3M CP 25WB+ (Red) and 3M CP15WB+ (Yellow). The WB25+ doesn't have any comment about the rigidity / flexibility, but the WB15+ says, "Dries to a firm, rubber-like solid".

They also sell 3M FD 150+ (blue, red, or limestone) is probably the best suited since it specifically states it makes a "flexible monolithic seal". Of course it's also the most expensive.
Stereodude is offline  
post #13 of 16 Old 08-10-2010, 01:48 PM
AVS Club Gold
 
SierraMikeBravo's Avatar
 
Join Date: Mar 2007
Location: Topeka, KS
Posts: 1,602
Mentioned: 5 Post(s)
Tagged: 0 Thread(s)
Quoted: 88 Post(s)
Liked: 65
Quote:
Originally Posted by Dennis Erskine View Post

Here's the best you can do (why am I telling people this? geeze, it takes money out of my pocket. Hey buddy, you got a buck for a cup of coffee?)


No kidding...why did I pay money? I could have just waitied until the question came up for free!

Shawn Byrne
Erskine Group
CEDIA Certified Professional EST II - HAA Level III Certified -THX Certified Professional

Design-Video & Audio Calibration Information

The original Pro Theater Layout
SierraMikeBravo is online now  
post #14 of 16 Old 08-10-2010, 03:35 PM
AVS Special Member
 
Elill's Avatar
 
Join Date: Dec 2007
Location: Sydney, Australia
Posts: 1,468
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 19 Post(s)
Liked: 22
Quote:
Originally Posted by ctviggen View Post

instead used 2 hour fire rated caulking

Thats what I'll be doing.....saying that, I got some recently for another thing I was making and well, its not nice stuff to work with. sticky, messy and takes AGES to dry......I guess thats the point...but its terrible compared to regular stuff.

Not sure what the consistency of silentseal is?......some people dont care about that stuff, but just a point to note

Peter the Greek

Downunder Theatre MkII
Redefining snail pace construction
"what is worth knowing is difficult to learn"

Elill is offline  
post #15 of 16 Old 08-10-2010, 04:21 PM - Thread Starter
Senior Member
 
WannaTheater's Avatar
 
Join Date: Aug 2006
Location: Tampa, FL
Posts: 492
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 2 Post(s)
Liked: 10
All, thanks for the information. Dennis, I owe you a dollar (I think a cup of coffee is now about 8 or 9 bucks at starbucks )

Quote:


When I finished off a room this year, the inspector specifically looked for fire-rated caulk in any hole in a header. In a wall, you could use whatever you wanted, but headers were a special case. He wasn't going to pass me unless it was fire-rated. The fire-rated caulk I see in lowes here is also colored bright red.

etk29321 - For me, the framing inspector checked to see if all of the header holes were plugged with the orange stuff..... which the were...
Or are you talking about the final inspection?
WannaTheater is offline  
post #16 of 16 Old 08-10-2010, 08:21 PM
AVS Special Member
 
snickel's Avatar
 
Join Date: Dec 2007
Location: South central Kansas
Posts: 1,158
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
I just did the hvac,plumbing and medical gas at a new dentist office, every hole in the top and bottom plate of a wall had to be fire caulked. We never have to do that on a single family home
snickel is offline  
Reply Dedicated Theater Design & Construction

Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page


Forum Jump: 

Posting Rules  
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off