Would you need an air return supply on a room that you were planning to install a mini-split AC system in? Our home uses baseboard heating so we don't have central A/C or it associated ductwork. To cool our basement theater I'm planning on putting in a mini-split A/C unit. To minimize sound leakage and intrusion I'd like to avoid putting in air supply/return lines in the room. I figure I can just leave the door open when its not in use to get fresh air in the room. Should that be adequate?
docquest is offline  
Sponsored Links
Advertisement
 
post #2 of 14 Old 08-16-2010, 11:31 AM
Member
 
ithunter's Avatar
 
Join Date: Feb 2009
Posts: 132
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 11
A mini split is a ductless system...basically a really nice window unit minus the window....it does have a line set that will need access to the condensing unit and most folks put those outside...
ithunter is offline  
post #3 of 14 Old 08-16-2010, 12:12 PM
HOME THEATER CONTRACTOR
 
BIGmouthinDC's Avatar
 
Join Date: Jan 2003
Location: Northern VA
Posts: 20,801
Mentioned: 5 Post(s)
Tagged: 1 Thread(s)
Quoted: 261 Post(s)
Liked: 608
What do you get when take a well built air tight theater space, a mini-split and a half a dozen people?

Answer: dead people, there is no fresh air.


To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
PROJECTS:
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
,
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
,
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
,
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
,
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
,
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
,
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
,
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
,

BIGmouthinDC is offline  
post #4 of 14 Old 08-16-2010, 12:18 PM
Senior Member
 
3fingerbrown's Avatar
 
Join Date: Aug 2009
Posts: 323
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
check out my build thread in my signature for how I tackled the problem of adding a return air fan to a room that had two supply vents and no return. For the most part I was able to add my return vent using sound isolation techniques. Good luck!

3FB's "Foreclosure" Theater:
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
3fingerbrown is offline  
post #5 of 14 Old 08-16-2010, 05:32 PM
AVS Special Member
 
snickel's Avatar
 
Join Date: Dec 2007
Location: South central Kansas
Posts: 1,158
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
Quote:
Originally Posted by BIGmouthinDC View Post

What do you get when take a well built air tight theater space, a mini-split and a half a dozen people?

Answer: dead people, there is no fresh air.

What he said^^^ you need to get fresh air in your room
snickel is offline  
post #6 of 14 Old 08-17-2010, 06:53 AM - Thread Starter
Member
 
docquest's Avatar
 
Join Date: Nov 2001
Posts: 95
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 12
Thanks for the feedback. Luckily I have easy access to adjoining rooms so adding a supply and a return shouldn't be too hard. I don't want to be in the headlines about the family that trapped in their own home theater like a bunch of coal miners. I just need to do it right so I don't negate all the effort of the double drywall, green glue, clips, etc. So for a 12x18x7.5 sized room do you think a reutn and a supply that were both 6" flexible insulated duct with a serpentine path would be enough?
docquest is offline  
post #7 of 14 Old 08-17-2010, 09:34 AM - Thread Starter
Member
 
docquest's Avatar
 
Join Date: Nov 2001
Posts: 95
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 12
Talk about perfect timing. I just saw the thread on examples of dead vents. I thought I researched all aspects of my theater build but I guess I missed the dead vents topic. The amount of knowledge and info sharing here is just fantastic.
docquest is offline  
post #8 of 14 Old 08-17-2010, 06:41 PM
AVS Special Member
 
snickel's Avatar
 
Join Date: Dec 2007
Location: South central Kansas
Posts: 1,158
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
Quote:
Originally Posted by docquest View Post

Thanks for the feedback. Luckily I have easy access to adjoining rooms so adding a supply and a return shouldn't be too hard. I don't want to be in the headlines about the family that trapped in their own home theater like a bunch of coal miners. I just need to do it right so I don't negate all the effort of the double drywall, green glue, clips, etc. So for a 12x18x7.5 sized room do you think a reutn and a supply that were both 6" flexible insulated duct with a serpentine path would be enough?

nope a 6" supply would need a 8" return air to remove same amount of air. I would start with 2 7" supplys and a 12" return air, and you may need more.
snickel is offline  
post #9 of 14 Old 08-17-2010, 06:49 PM
AVS Special Member
 
snickel's Avatar
 
Join Date: Dec 2007
Location: South central Kansas
Posts: 1,158
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
Ok I was wrong you said you had no ac so you are just using the dead vents for fresh air so yes a 6" supply and a 6" return air will work
snickel is offline  
post #10 of 14 Old 01-19-2011, 05:09 PM
Senior Member
 
uscmatt99's Avatar
 
Join Date: Apr 2010
Posts: 309
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 12
I just found this thread while searching for ideal minisplit systems to use for my theater. I've been working with the HVAC guy doing the rest of my house, and we concluded that a minisplit system would be the easiest way to cool the theater room while allowing heat to the rest of the house for our cool Michigan winters.

Unfortunately neither the builder or the HVAC guy have done theater rooms with the degree of sound isolation we have planned. Glad I found this thread, or I wouldn't have been around to tell you all how my theater turned out! I'm going to work with them on designing a dead vent system for the room.

On another note, after a long discussion, it looked like it was going to be a royal pain to take a zone off of the rest of the HVAC to adequately cool the room, so we're still going with a minisplit. Any brand recommendations for the quietest system? The best I found was a Sanyo that was at around 25-38 dB depending on fan speed.
uscmatt99 is offline  
post #11 of 14 Old 06-16-2014, 11:28 AM
AVS Special Member
 
BrolicBeast's Avatar
 
Join Date: Sep 2009
Location: Charles County, MD
Posts: 2,934
Mentioned: 1 Post(s)
Tagged: 0 Thread(s)
Quoted: 180 Post(s)
Liked: 306
Quote:
Originally Posted by BIGmouthinDC View Post
What do you get when take a well built air tight theater space, a mini-split and a half a dozen people?

Answer: dead people, there is no fresh air.
I guess this answers the mini-split v.s. dead vent debate.

Dead Vent it is.

The Build:
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
| The System:
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
| The Video Series:
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.


Social:
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
|
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
|
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
|
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
|
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
BrolicBeast is online now  
post #12 of 14 Old 06-16-2014, 11:48 AM
AVS Club Gold
 
LeBon's Avatar
 
Join Date: Jun 2006
Location: Pebble Beach, CA
Posts: 673
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 26 Post(s)
Liked: 30
I'll be using a Ducted mini-split, so that I can also use it to bring in fresh air. It also gets the fan noise out of the room.


To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
LeBon is offline  
post #13 of 14 Old 06-16-2014, 01:10 PM
Senior Member
 
kmhvball's Avatar
 
Join Date: Mar 2014
Location: Mason, Ohio
Posts: 250
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 61 Post(s)
Liked: 42
I am planning a Mini-Split for the Heating/Cooling Needs, and am doing a separate dead vent type 'air supply' into the room for fresh air.

I didn't want to tap into my main system for sound concerns.

I am still figuring out the Air Return, I will use my current system, there are a few 90 degree bends before the main supply lines. I just now need to do research on 'how' to tap into a Return!

Kevin

Thanks!

Kevin


To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
kmhvball is offline  
post #14 of 14 Old 06-16-2014, 04:14 PM
AVS Club Gold
 
LeBon's Avatar
 
Join Date: Jun 2006
Location: Pebble Beach, CA
Posts: 673
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 26 Post(s)
Liked: 30
The air handler for the ducted mini-split is separate from your "main" system. You can run the supply and return from the duct mini-split air handler through dead vents to control sound. You can also pull in outside sir to the air handler for fresh air.


To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
LeBon is offline  
Reply Dedicated Theater Design & Construction

User Tag List

Thread Tools
Show Printable Version Show Printable Version