Breaker problems- Annoyed - AVS Forum
Forum Jump: 
 
Thread Tools
post #1 of 4 Old 10-15-2013, 04:33 PM - Thread Starter
Member
 
rthompson10's Avatar
 
Join Date: Mar 2009
Posts: 76
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
After 3 years with the basement up and running I started having breaker issues on Sunday, with the breaker controlling my electronics and the breaker supporting my theater lights constantly tripping.
I had an electrician in yesterday and he checked all outlets, tightened a couple of things and I thought I was good to go. BUT same thing today.

The 2 breakers are AFCI breakers per code but given all of my reading and discussions with electricians I'm going back to standard breakers.

Anyone run into this before? I was just sitting watching football then nothing

RT
rthompson10 is offline  
Sponsored Links
Advertisement
 
post #2 of 4 Old 10-15-2013, 05:03 PM
AVS Special Member
 
Pain Infliction's Avatar
 
Join Date: Jun 2010
Location: Houston Texas
Posts: 2,707
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 157 Post(s)
Liked: 198
Are the breakers tripping at the same time? Are they in the main breaker box or is there a dedicated box for your theater? Little more info will help.

MY THEATER......The Thompson Theater 11.9 channels

"Is not love not unlike the unlikely not it is unlikened to?"
- Leon Phelps
Pain Infliction is offline  
post #3 of 4 Old 10-15-2013, 05:36 PM - Thread Starter
Member
 
rthompson10's Avatar
 
Join Date: Mar 2009
Posts: 76
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
The breakers aren't tripping at the same time. There is a 100A panel off of the main sub panel that contains all of the breakers for the basement including the 2 that are tripping. Nothing truly special as far as equipment- Denon receiver, bluray, couple of cable boxes, PS3
The other breaker controls the theater lights- 4 sconces, 7 high hats, rope light- all on dimmers
rthompson10 is offline  
post #4 of 4 Old 10-15-2013, 05:48 PM
AVS Special Member
 
Pain Infliction's Avatar
 
Join Date: Jun 2010
Location: Houston Texas
Posts: 2,707
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 157 Post(s)
Liked: 198
It is weird that both breakers are doing this but it just sounds like they are bad. I would start with that and just replace them like you said you were going to do. You do not need an electrician to do it. It is easy and should only cost you the what the breakers are. Just make sure you kill the power on your 100A circuit. I couldn't imagine it being anything else. There is no way that you are pulling too many amps unless you have massive amps to drive your subs, but you would get the breaker tripping at obvious points. plus that has nothing to do with the lights. Probably not a short somewhere because you would know that as well and it would have to be on both circuits.

MY THEATER......The Thompson Theater 11.9 channels

"Is not love not unlike the unlikely not it is unlikened to?"
- Leon Phelps
Pain Infliction is offline  
Reply Dedicated Theater Design & Construction

User Tag List

Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page


Forum Jump: 

Posting Rules  
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off