Hi-
I'm, mounting a pair of in ceiling speakers and I have been trying to figure out waht to use for the speaker wire - I'm estimating I'll need approximately 35 - 45 ft of wire to each speaker - Based on that, I was thinking a CMP (Plenum) 14 gauge wire - Any thoughts?

Can someone recommend a good wire to use?

Thanks!
Jeremybe is offline  
Sponsored Links
Advertisement
 
post #2 of 15 Old 12-31-2006, 12:35 PM
AVS Special Member
 
trekguy's Avatar
 
Join Date: Nov 2005
Location: West of Mt Diablo
Posts: 2,192
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
14 AWG should be fine. Any brand should be fine.

Could be sold as speaker wire, or lamp cord or zip cord or low voltage lighting cable. Many get the cheapest from the local hardware or home center. If any part of your run is inside of a wall you might want to get wire rated for in wall use (fire safety not an audio issue).

The fact that an opinion has been widely held is no evidence whatever that it is not utterly absurd.
-Bertrand Russell
trekguy is offline  
post #3 of 15 Old 01-01-2007, 05:44 PM
Senior Member
 
fedders's Avatar
 
Join Date: Jul 2006
Location: Chicago, IL
Posts: 418
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 1 Post(s)
Liked: 11
Quote:
Originally Posted by trekguy View Post

14 AWG should be fine. Any brand should be fine.

Could be sold as speaker wire, or lamp cord or zip cord or low voltage lighting cable. Many get the cheapest from the local hardware or home center. If any part of your run is inside of a wall you might want to get wire rated for in wall use (fire safety not an audio issue).

Agreed on the 14 AWG and that any brand will work fine. But, you will need something rated for in-wall. CL2, CL3 or CM, CMR ratings are what you should look for assuming this is a home. Plenum (CMP) is not needed as you are not installing the cable into a Plenum air handling space. (But check with your local inspector - if you have a permit for this install)

Carl Fedders

Carl Fedders
fedders is offline  
post #4 of 15 Old 01-02-2007, 08:20 AM - Thread Starter
Member
 
Jeremybe's Avatar
 
Join Date: Apr 2006
Posts: 57
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
Thanks for the replys! 14 Awg non-plenum it is - Appreciate it!
Jeremybe is offline  
post #5 of 15 Old 01-03-2007, 09:45 AM
Member
 
3000GTCSULB's Avatar
 
Join Date: Jan 2007
Posts: 17
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
Pictures of setup?
3000GTCSULB is offline  
post #6 of 15 Old 01-12-2007, 05:29 AM
 
flags's Avatar
 
Join Date: Dec 2006
Posts: 471
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
If for any reason you have a house fire and they find you were not using the correct wire your insurance company may not pay. Any in wall or ceiling installation must use in-wall rated wire.
flags is offline  
post #7 of 15 Old 01-13-2007, 05:12 AM
AVS Special Member
 
DougRuss's Avatar
 
Join Date: Oct 2001
Location: Northern Indiana
Posts: 1,373
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
Quote:
Originally Posted by flags View Post

If for any reason you have a house fire and they find you were not using the correct wire your insurance company may not pay. Any in wall or ceiling installation must use in-wall rated wire.


Only if it was the source of the fire !
DougRuss is offline  
post #8 of 15 Old 01-15-2007, 10:26 AM
Member
 
sport06's Avatar
 
Join Date: Dec 2002
Location: Westminster, MD
Posts: 101
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
Quote:
Originally Posted by flags View Post

If for any reason you have a house fire and they find you were not using the correct wire your insurance company may not pay. Any in wall or ceiling installation must use in-wall rated wire.


There is no such thing as "in-wall" rated cables. CL2 and CL3 are general purpose!

Robert Hansen, RCDD
sport06 is offline  
post #9 of 15 Old 01-15-2007, 03:03 PM
Newbie
 
superscott's Avatar
 
Join Date: Jan 2007
Location: Dallas, Tx.
Posts: 4
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
He's right guys... either its plenum rated or its not. I wouldn't recommend 'lamp cord'. Any liberty, bleden, westpenn.. will do. The only diff is that non-plenum rated wire has a pvc jacket, this type of jacket has a toxic smoke when it is burned.
superscott is offline  
post #10 of 15 Old 01-16-2007, 08:10 AM
AVS Special Member
 
video321's Avatar
 
Join Date: Jun 2002
Location: NJ
Posts: 1,578
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 5 Post(s)
Liked: 14
I really do wish I understood this better. Why is it so hard to find info?
It does seem, though, that any low-voltage cable with a simple UL listing may be used in residential walls. Of course, I'm not positive about that

I did find this article from Extron:
Wire Ratings

If this is the case, then even my USB cable is rated for in-wall (its UL CM, the same as a box of CAT5e)
video321 is offline  
post #11 of 15 Old 01-16-2007, 04:12 PM
Newbie
 
superscott's Avatar
 
Join Date: Jan 2007
Location: Dallas, Tx.
Posts: 4
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
There are many many different UL Marking found on devices. They have different meanings. UL (Underwriters Labratories, Inc.) just verifies that the product has been tested to meet a certain standard (safety, data transmission, etc.) then puts their stamp of approval on it. Doesnt have anything to do with Plenum or non plenum usage.
superscott is offline  
post #12 of 15 Old 01-16-2007, 08:16 PM
Member
 
sport06's Avatar
 
Join Date: Dec 2002
Location: Westminster, MD
Posts: 101
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
Quote:
Originally Posted by superscott View Post

There are many many different UL Marking found on devices. They have different meanings. UL (Underwriters Labratories, Inc.) just verifies that the product has been tested to meet a certain standard (safety, data transmission, etc.) then puts their stamp of approval on it. Doesnt have anything to do with Plenum or non plenum usage.

ABSOLUTELY DEAD WRONG!

UL has 4 different markings: Recognized, Listed, Classified, and Verified.

Recognized is for a specific component in a listed device or package

Listed products have completed a series of mechanical, electrical and thermal characteristics tests which simulate reasonable and foreseeable hazards.

Classified products undergo further tests for specific hazards, performance tests under specified conditions, regulatory code requirements,

Verified marking are performance based tests as part of a specific system

Listed cables have been tested in accordance NFPA requirements for flame propogation.

The only difference between CMR (riser) and CMP (plenum) is their flame propogation properties. Riser rated cables are suitable for vertical shafts and non-air return spaces. Plenum rated cables are suitable for return air plenums. They are basically made from the same "ingredients", just different quantities of them.

Audio Visual cables are typically marked CL2 and CL3, CL2R and CL3R, CL2P and CL3P

STAY AWAY FROM ANTHING MARKED WITH AN "x"! (CMX, CLX, etc)

And yes, CM rated cables are fine for residential use. Usually though, Cat5e cables are CMR or CMP. CM is mostly reserved for patch cables.

And yes again, residential construction does not have the requirements that commercial construction has. Most jurisdictions dont even have permit requirements for low voltage cabling.

Robert Hansen, RCDD
sport06 is offline  
post #13 of 15 Old 01-17-2007, 02:32 AM
Member
 
sport06's Avatar
 
Join Date: Dec 2002
Location: Westminster, MD
Posts: 101
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
Quote:
Originally Posted by video321 View Post

I really do wish I understood this better. Why is it so hard to find info?
It does seem, though, that any low-voltage cable with a simple UL listing may be used in residential walls. Of course, I'm not positive about that

I did find this article from Extron:
Wire Ratings

If this is the case, then even my USB cable is rated for in-wall (its UL CM, the same as a box of CAT5e)


go to www.ul.com and search for the Wire and Cable Marking Guide. Its a free PDF, provides lots of information, and will help you for your search for information.

Robert Hansen, RCDD
sport06 is offline  
post #14 of 15 Old 01-28-2007, 03:10 PM
Newbie
 
superscott's Avatar
 
Join Date: Jan 2007
Location: Dallas, Tx.
Posts: 4
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
WOW!

was I really ABSOLUTELY DEAD WRONG ? or was I just wrong about the plenum part?


jerkoff.
superscott is offline  
post #15 of 15 Old 01-28-2007, 03:42 PM
 
flags's Avatar
 
Join Date: Dec 2006
Posts: 471
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Liked: 10
crutchfield.com has lots of info and you can send them an email question and they will answer it for you.
flags is offline  
Reply Tweaks and Do-It-Yourself

User Tag List

Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page


Forum Jump: 

Posting Rules  
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off