In yet another “help a friend” project, I am concerned about how the 240v feed was done to their electric water heater. The wire size (10ga) and breaker (2 pole 30amp) are correct per the NEC for the wattage rating of the heater, but the way the feed connection to the heater was done concerns me. The feed wire comes out of the subpanel – goes up into the floor joists, then across to the heater (about 6 feet – all OK so far), but then the wire just drops out of the floor joists, unsupported for 5 feet and is connected to the heater. Should this drop cable be in BX? Can a non-metallic “armored” cable be used? Saw this: http://www.acehardwaresuperstore.com...00.html?ref=42
AVS › AVS Forum › Home Entertainment & Theater Builder › Dedicated Theater Design & Construction › Electric water heater wiring code question
Electric water heater wiring code question
AVS Top Picks
post #2 of 23
6/28/09 at 8:03am
post #3 of 23
6/28/09 at 8:40am
post #4 of 23
6/28/09 at 8:47am
post #5 of 23
6/28/09 at 8:50am
post #6 of 23
6/28/09 at 9:07am
post #7 of 23
6/28/09 at 11:35am
post #8 of 23
6/28/09 at 12:09pm
post #9 of 23
6/28/09 at 1:39pm
post #10 of 23
6/28/09 at 6:28pm
post #11 of 23
6/29/09 at 7:44pm
post #12 of 23
6/30/09 at 1:43am
post #13 of 23
6/30/09 at 5:16am
post #15 of 23
6/30/09 at 11:58pm
post #16 of 23
2/6/13 at 5:43pm
post #17 of 23
2/6/13 at 5:56pm
post #18 of 23
2/6/13 at 6:00pm
post #19 of 23
2/6/13 at 6:37pm
post #20 of 23
2/6/13 at 8:45pm
post #21 of 23
2/7/13 at 6:03am
post #22 of 23
2/7/13 at 11:23am
post #23 of 23
2/7/13 at 12:33pm
AVS Top Picks
AVS › AVS Forum › Home Entertainment & Theater Builder › Dedicated Theater Design & Construction › Electric water heater wiring code question













Thanks for the input guys.