I have a pn64d8000 that is causing the voltage on the circuit it's on to dip every time it goes from dark to light. Seems to be worst after it transitions from commercials. I first noticed a light flickering that was on the same circuit and after checking neutrals, grounds and back stabs etc i finally found that it was the tv. I've seen power conditioners like the Furman's but was wondering if a conditioner or regulator would keep the line voltage stable...or are they only there to protect the tv? Any idea what product or suggestion that could fix this problem?
AVS › AVS Forum › Display Devices › Plasma Flat Panel Displays › Samsung pn64d8000 causing voltage dips
Featured Stories
Topics Discussed
Related Forum Threads
- Need advice between JBL and Jamo speakers Last post on 3/4/13 at 10:24am in Speakers
- Samsung PN64D8000 64? Last post on 11/23/12 at 5:26pm in Great Found Deals
- ARC on PN64D8000 Last post on 11/3/12 at 8:44am in Plasma Flat Panel Displays
- Onkyo SR508 Intermittant Playing 3D Blu-rays from Panasonic BDT210 to Samsung PN64D8000 Last post on 10/6/12 at 7:35am in Receivers, Amps, and Processors
- Giving the choice of PN64D8000 vs TC-P65GT50 which would be the choice based on PQ Last post on 9/10/12 at 2:37pm in Plasma Flat Panel Displays
Related Reviews
Samsung pn64d8000 causing voltage dips
Gear mentioned in this thread:
post #2 of 7
2/23/13 at 10:04pm
- RandyWalters
- Trader Feedback: 0
- Doesn't Read PMs
-
- offline
- 16,263 Posts. Joined 2/2003
- Location: El Segundo, Calif
- Select All Posts By This User
It kinda sounds like maybe that circuit is already heavily loaded with other devices, and adding a 500 watt TV may be the straw that is breaking the camel's back.
1. How many amps is the circuit breaker for that circuit?
2. Besides the TV, list all of the other devices that are on that circuit.
3. That light that's flickering when the TV is displaying bright scenes - is that a table lamp that's plugged into the same circuit as the TV? Or is it a ceiling light that's on a different circuit ?
1. How many amps is the circuit breaker for that circuit?
2. Besides the TV, list all of the other devices that are on that circuit.
3. That light that's flickering when the TV is displaying bright scenes - is that a table lamp that's plugged into the same circuit as the TV? Or is it a ceiling light that's on a different circuit ?
1) 15A
2) 4-rec light cans,bathroom light
Then there are a couple of outlets - subwoofer, a reciever ...
3) it's the lights on that circuit that flicker
I can just run the tv and the lights, nothing else, and it does it.
The breaker is a arc fault (acfi) which suck IMO. I'm going to swap it with another one and see if that's it.
2) 4-rec light cans,bathroom light
Then there are a couple of outlets - subwoofer, a reciever ...
3) it's the lights on that circuit that flicker
I can just run the tv and the lights, nothing else, and it does it.
The breaker is a arc fault (acfi) which suck IMO. I'm going to swap it with another one and see if that's it.
post #4 of 7
2/24/13 at 9:02am
- budwich
- Trader Feedback: 0
-
- offline
- 1,077 Posts. Joined 12/2002
- Location: Kanata, Ontario, Canada
- Select All Posts By This User
post #5 of 7
2/24/13 at 3:19pm
- RandyWalters
- Trader Feedback: 0
- Doesn't Read PMs
-
- offline
- 16,263 Posts. Joined 2/2003
- Location: El Segundo, Calif
- Select All Posts By This User
Well you didn't quite answer all my questions but one glaring thing is that there should not be any wall plugs on an overhead ceiling light circuit - wall circuits usually have 20 amp breakers and are always separate from ceiling light circuits (which usually have 15 amp breakers).
Did someone (like an un-licensed electrician?) do some rewiring in your house in recent years or some sort of room addition or renovation where circuits were added or tapped into? Arc-Fault breakers work just fine and i've supplied hundreds of them to electricians without a single issue, so if you're having an issue with it then it was probably not installed/wired correctly, which might explain why you're able to plug stuff into the same circuit as your recessed lights - that doesn't happen in my industry.
Changing the Arc-Fault breaker won't accomplish anything as it's not the cause of the problem, so don't bother. The problem is with the circuit that it's sending voltage to - specifically the fact that wall plugs are connected to a ceiling light circuit.
Did someone (like an un-licensed electrician?) do some rewiring in your house in recent years or some sort of room addition or renovation where circuits were added or tapped into? Arc-Fault breakers work just fine and i've supplied hundreds of them to electricians without a single issue, so if you're having an issue with it then it was probably not installed/wired correctly, which might explain why you're able to plug stuff into the same circuit as your recessed lights - that doesn't happen in my industry.
Changing the Arc-Fault breaker won't accomplish anything as it's not the cause of the problem, so don't bother. The problem is with the circuit that it's sending voltage to - specifically the fact that wall plugs are connected to a ceiling light circuit.
Quote:
Originally Posted by RandyWalters 
Well you didn't quite answer all my questions but one glaring thing is that there should not be any wall plugs on an overhead ceiling light circuit - wall circuits usually have 20 amp breakers and are always separate from ceiling light circuits (which usually have 15 amp breakers).

Well you didn't quite answer all my questions but one glaring thing is that there should not be any wall plugs on an overhead ceiling light circuit - wall circuits usually have 20 amp breakers and are always separate from ceiling light circuits (which usually have 15 amp breakers).
Don't like bashing someone trying to help me out but I've never heard of that, it's not code to do it like that its only recommend to wire them separately in case you pop a outlet you won't be left in the dark...as far as "always" being separate no way. And I've seen plenty of houses with 15A outlets...that's also not code. What contractor is going to splurge for 12/2 and 20A outlets when they can get away with 15A and 14/2 just fine.
House is new and was wired by a lic elect
But regardless...I took one of the standard non grfi,non acfi breakers out of the panel and wired it in...no flicker and steady voltage....so bad acfi breaker it is. $50 POS!!!
post #7 of 7
2/25/13 at 7:00am
- RandyWalters
- Trader Feedback: 0
- Doesn't Read PMs
-
- offline
- 16,263 Posts. Joined 2/2003
- Location: El Segundo, Calif
- Select All Posts By This User
Quote:
Originally Posted by 2000xpsd 
Don't like bashing someone trying to help me out but I've never heard of that, it's not code to do it like that its only recommend to wire them separately in case you pop a outlet you won't be left in the dark...as far as "always" being separate no way. And I've seen plenty of houses with 15A outlets...that's also not code. What contractor is going to splurge for 12/2 and 20A outlets when they can get away with 15A and 14/2 just fine.
House is new and was wired by a lic elect
But regardless...I took one of the standard non grfi,non acfi breakers out of the panel and wired it in...no flicker and steady voltage....so bad acfi breaker it is. $50 POS!!!

Don't like bashing someone trying to help me out but I've never heard of that, it's not code to do it like that its only recommend to wire them separately in case you pop a outlet you won't be left in the dark...as far as "always" being separate no way. And I've seen plenty of houses with 15A outlets...that's also not code. What contractor is going to splurge for 12/2 and 20A outlets when they can get away with 15A and 14/2 just fine.
House is new and was wired by a lic elect
But regardless...I took one of the standard non grfi,non acfi breakers out of the panel and wired it in...no flicker and steady voltage....so bad acfi breaker it is. $50 POS!!!
What were the voltage readings you were getting from that Arc-fault breaker before you removed it? Were they fluctuating? With or without a load?
I have been in the Electrcial Contractor industry for 38 years (mostly in the wholesale end but also have done wiring) and it's a fact that at least here in California, ceiling circuits are always separate from wall circuits. They are never combined. I think this is dictated in the NEC but not sure, and not sure if wall and ceiling circuits are combined in other states. But we sell 5 rolls of 12/2 Romex to every one roll of 14/2 (i do sales and i stock the store up so i know), and they always use 12/2 and 20 amp breakers for the wall circuits and only use 14/2 with 15 amp circuits for the ceiling circuits. And these circuits are never combined. Ever. There has to be a reason why we never combine them here - and i don't think it's just a California thing. And the wall receptacles are always 15 amp - this is allowed on a 20 amp breaker as long as the receptacles are side-wired and i believe that they do this because they can put more receptacles on a 20 amp circuit than they can on a 15 amp circuit so that would actually save money. The 20 amp wall receptacles are usually used on single dedicated circuits (washing machine, microwave oven, dish washer) and are the only receptacle on that circuit. This goes for multi-unit apartment buildings, condos, townhomes, and single family homes ranging from 2-bedroom to 6-bedroom beach houses from Palos Verdes to Malibu. I do the material list take-offs directly from the construction plans and this is how all the homes are engineered.
Either you live in Canada (they use 14/2 for wall circuits and ceiling circuits), or your electrician wired some circuits wrong. I know dozens of licensed electricians that i would not allow to wire my house, they're that bad. I can't tell you how many horror stories we've heard from electricians who were correcting previous incorrectly done work performed by licensed electricians. Hell, my best friend's 3-room addition was wired by a licensed electrician but upon final inspection he had 13 corrections on the notice that had to be corrected. And one of em was he'd tapped into a wall circuit to wire the overhead can lights in a guest bathroom and it was against code. It took us two weekends to correct all the stupid stuff this licensed and so-called "Title 24 Specialist" did incorrectly. He was a moron.
I think that your arc-fault breaker was having issues because the shared ceiling/wall circuit is not wired correctly, possibly an issue with a shared neutral somewhere. An Arc-fault breaker is much more sensitive to wiring issues where a regular breaker isn't affected, so by removing the Arc-fault you're taking a band-aid approach to a bigger problem. Arc-fault breakers (and GFCI breakers) are pre-tested before they leave the assembly line by law, and i have never ever gotten one back defective (Murray, ITE, Cutler Hammer, GE). Your issue has to be a problem with the way that circuit is wired.
I really think you need to get a 2nd opinion from a licensed and competent electrician, it won't take him long at all to trouble-shoot the issue and find the cause. House wiring is super easy.
___________________________________
Edited by RandyWalters - 2/25/13 at 7:20am
Return Home
Back to Forum: Plasma Flat Panel Displays
- Samsung pn64d8000 causing voltage dips
AVS › AVS Forum › Display Devices › Plasma Flat Panel Displays › Samsung pn64d8000 causing voltage dips
Currently, there are 1661 Active Users
(409 Members and 1252 Guests)
Recent Discussions
- › Lilmike's LilWrecker 8 seconds ago
- › Has the Panasonic 3d1 been discontinued? 38 seconds ago
- › Which Album (CD or Vinyl) Are you listening to now 42 seconds ago
- › Master Burn-In/IR/Break In Thread Part II: All Posts Here Only 50 seconds ago
- › ?s about front towers 58 seconds ago
- › Newbie here- Please help me assemble this.. 1 minute ago
- › DIY Custom-Printed Movie Poster Acoustic Panels - cheap! 1 minute ago
- › Darbee vision darblet 1 minute ago
- › FS HDHOMERUN Prime 3CC 2 minutes ago
- › Microsoft fires the first shot in the "NEXT" generation.... 2 minutes ago
View: New Posts | All Discussions
Recent Reviews
- › Epson V11H501020 PowerLite Home Cinema 3020 2D and 3D 1080p Home... by sailorb
- › BenQ W1070 1080P 3D Projector by jakob_s
- › Elite Screens ER110WH1 Sable Fixed Frame (110" 16:9 AR) by DDT0C
- › Elite Screens ER100WH1-A1080P2 Sable Fixed Frame Projection Screen by DDT0C
- › Peerless PRG Mount, Black by DDT0C
- › Epson 5020UB Powerlite Home Cinema 3D Front Projector by DDT0C
- › Sony VPLHS20 Cineza Digital Home Entertainment LCD Projector by varkeast
- › JVC DLA-RS45 Home Theater Projector 1080P HDMI by jmccarei
- › Sharp DT 510 DLP Projector by rdcollns
- › Onkyo TXNR801 / TX-NR801 / TX-NR801 7.1 Channel Digital Home... by mswope63
View: More Reviews
New Articles
- › Projector Review Contest by Nick Val
- › "List Your Gear to Win Some Gear"... by Nick Val
- › Most Economical Thin Client PC`s from RDP... by RDPThinClients
- › Media Browser 3 Announced by xzener
- › AVS Guide to Media Servers, Part 1 by Scott Wilkinson
- › Join the AVS Team! by Nick Val
- › 25 Top Blu-ray releases for 2012 by Ralph Potts
- › Sony Launches 4k Ultra HD Flat Panel - AVS... by Scott Wilkinson
- › Clarus Power Cords by Good Tunes
- › A Theater Is Just Is Not A Theater, Unless... by David Bott
View: New Articles | All Articles
Home | Reviews | Forums | Articles | My Profile
About AVS | Join the Community | Advertise | Contact Us
© 2013 AVS is powered by Huddler Tech | FAQ | Support | Privacy/TOS | Site Map
About AVS | Join the Community | Advertise | Contact Us
© 2013 AVS is powered by Huddler Tech | FAQ | Support | Privacy/TOS | Site Map



![Samsung PN64D8000 64-Inch 1080p 600Hz 3D Plasma TV [2011 MODEL]](http://cdn.avsforum.com/1/1c/50x50px-ZC-1c92d0f5_B004RTE5BA-31bAG72Yj6L.jpeg)



