I have the following circuits available to my basement:
(A) 1 - 20A (Currently 12/2 dead-end in blank box)
(B) 1 - 20A (Currently 12/2 to outlets including GFI)
(C) 1 - 15A (Currently 14/2 to 3 standard light bulb fixtures)
(D) 2 - 15A (Currently 14/3 to dead-end in blank box)
What I found odd was that the electricians ran a 14/3 off of two different 15A breakers, non-interlocking...So, I have one romex with 2 hots that share one neutral and one ground wire. I'd seen this done for 220V circuits with interlocking breakers, but not for two 110V circuits...
Anyway.
My plan is as follows:
(A) Equipment Rack + Projector (Panasonic 75u)
(B) Change to Outlets for HT (2 Subs, conv duplex, possible elec screen)
(C) Change to Lights for HT (10 Cans, 5 sconces, Dimmers)
(D1) One leg of 14/3 - Lights for non-HT areas (5 Cans, 2 Utility closet lights, 2 Ceiling Fans, 1 Track Lighting)
(D2) 2nd leg of 14/3 - Outlets for non-HT (1GFI, 8 duplex)
Firstly, does this look like a good arrangement of circuits, and secondly does it meet NEC load requirements.
EDIT:
I was doing some more research and ran across this post by Brucer:
max wire feet @ 120 volts, 1 phase, 2% max voltage drop:
15 amp #14=30' #12=47' #10=75' #8=120'
20 amp #14=.... #12=36' #10=57' #8=90'
30 amp #14=.... #12=.... #10=38' #8=60'
Is this a code requirement, or more of a performance guideline for not dropping your voltage to your AV equipment. My Basement is 30' long, and the breaker panel is on one end. The electrician's ran all #14 for 15 amp circuits. Now, the 15A circuits are only destined for general duty use (outlets and lights), but the entire circuit would certainly exceed 30 feet.
Lastly, what is the rule for splitting runs? Do you have to start at one device and end at the last one? For example, my services come into one corner of the basement...I have lights down both walls perpendicular to this corner...Do I have to go down one wall, loop back up and then down the other, or can I go to the first device, and split two feeds (#1 and #2) from there going back with #1 to service the other wall, and continue down with #2 on the existing wall?
(A) 1 - 20A (Currently 12/2 dead-end in blank box)
(B) 1 - 20A (Currently 12/2 to outlets including GFI)
(C) 1 - 15A (Currently 14/2 to 3 standard light bulb fixtures)
(D) 2 - 15A (Currently 14/3 to dead-end in blank box)
What I found odd was that the electricians ran a 14/3 off of two different 15A breakers, non-interlocking...So, I have one romex with 2 hots that share one neutral and one ground wire. I'd seen this done for 220V circuits with interlocking breakers, but not for two 110V circuits...
Anyway.
My plan is as follows:
(A) Equipment Rack + Projector (Panasonic 75u)
(B) Change to Outlets for HT (2 Subs, conv duplex, possible elec screen)
(C) Change to Lights for HT (10 Cans, 5 sconces, Dimmers)
(D1) One leg of 14/3 - Lights for non-HT areas (5 Cans, 2 Utility closet lights, 2 Ceiling Fans, 1 Track Lighting)
(D2) 2nd leg of 14/3 - Outlets for non-HT (1GFI, 8 duplex)
Firstly, does this look like a good arrangement of circuits, and secondly does it meet NEC load requirements.
EDIT:
I was doing some more research and ran across this post by Brucer:
max wire feet @ 120 volts, 1 phase, 2% max voltage drop:
15 amp #14=30' #12=47' #10=75' #8=120'
20 amp #14=.... #12=36' #10=57' #8=90'
30 amp #14=.... #12=.... #10=38' #8=60'
Is this a code requirement, or more of a performance guideline for not dropping your voltage to your AV equipment. My Basement is 30' long, and the breaker panel is on one end. The electrician's ran all #14 for 15 amp circuits. Now, the 15A circuits are only destined for general duty use (outlets and lights), but the entire circuit would certainly exceed 30 feet.
Lastly, what is the rule for splitting runs? Do you have to start at one device and end at the last one? For example, my services come into one corner of the basement...I have lights down both walls perpendicular to this corner...Do I have to go down one wall, loop back up and then down the other, or can I go to the first device, and split two feeds (#1 and #2) from there going back with #1 to service the other wall, and continue down with #2 on the existing wall?