Discussion Starter · #1 ·
I need advice on the best surge protectors and grounding adapters for 2 prong low voltage transformers (ranging from 12-24 VAC output) as well as my LAN data lines (RG45). I am told I need to ensure the transformers themselves are grounded in spite of their 2 prong plugs. I have been plagued by surge destruction of numerous circuit boards on all of my systems. I just had the entire house encased in a sophisitcated grounding system and am now trying to isolate individual weak spots.
 

·
Registered
Joined
·
7,822 Posts