I'm wiring the low-voltage side of my Grafik Eye system and I have the Lutron GRX-CBL-346S cable (thank you, Dennis). Note the 24 AWG drain wire. The installation instructions make no note of it. Should it be tied to common ground? Ignored?
 

·
Registered
Joined
·
7,822 Posts
Discussion Starter · #2 ·
Try again.
 

·
Registered
Joined
·
7,822 Posts
Discussion Starter · #3 ·
Correction to the previously posted "correct" answer: On p.5 of the Installer's Guide for Models MR and IA, under 'Mounting', there is this note:
Quote:
3. Connect two ... pairs for Class 2/PELV wiring (daisy-chain between stations)â€*.


â€* If shielded wire is used, the drain wire must also be daisy-chained. Do not connect drain wire to earth/ground or Accessory Control (unless a "D" terminal is present).
 

·
Registered
Joined
·
7,822 Posts
Discussion Starter · #4 ·
bump to show correction
 