My heat loss calculations indicated that my theater room may not need much heat if any - in fact I think I will need some cooling/ventillation with more than two people.
The attached floorplan shows the proposed home theater (bottom of floorplan).
The two walls adjacent to the foundation will be normal 2x4 insulated stud walls - R13. The two interior walls will be double walls - R25 (or so). A good amount of the floor is insulated due to stage and riser coverage.
Floor is poured concrete about 4' underground.
New England location (MA). The basement in its current unfinished state is a steady 60 year round.
My heat loss calcs indicate that I will need about 900 BTU/Hr to maintain +10 deg. F. or 70 deg. F. The projector and a single person should generate this (Projector with 250W bulb perhaps 600 BTU/Hr; each human 200-300 BTU/Hr).
Thus, forget a heater for long, with more than two people (and there will be seating for up to 8), we will need cooling or ventillation.
Instead of bona-fide air conditioning, I though perhaps some forced air circulation to the adjacent basement space which will require about 4000 BTU/Hr of heat. I am concerned about defeating the sound isolation with ductwork. I am more concerned about sound to/from upstairs than into the adjacent basement space.
I thought perhaps a 3-500cfm in-line remote blower (bathroom exhaust type) would do the trick. It would suck air from a duct high in the interior partition double wall at the theater front and flex snaked down the wall and out the other side bottom into a closet in the adjacent basement space where the fan will be for noise isolation which will discharge the warm theater air into the adjacent basement space out another of the closet walls into the adjacent space. Same scheme at the other end of the theater for intake air (but no blower - this will be how air from the adjacent basement gets in).
Any other thoughts/tricks? Do my heat calcs seem reasonable?
How do others deal with this issue?
db

The attached floorplan shows the proposed home theater (bottom of floorplan).
The two walls adjacent to the foundation will be normal 2x4 insulated stud walls - R13. The two interior walls will be double walls - R25 (or so). A good amount of the floor is insulated due to stage and riser coverage.
Floor is poured concrete about 4' underground.
New England location (MA). The basement in its current unfinished state is a steady 60 year round.
My heat loss calcs indicate that I will need about 900 BTU/Hr to maintain +10 deg. F. or 70 deg. F. The projector and a single person should generate this (Projector with 250W bulb perhaps 600 BTU/Hr; each human 200-300 BTU/Hr).
Thus, forget a heater for long, with more than two people (and there will be seating for up to 8), we will need cooling or ventillation.
Instead of bona-fide air conditioning, I though perhaps some forced air circulation to the adjacent basement space which will require about 4000 BTU/Hr of heat. I am concerned about defeating the sound isolation with ductwork. I am more concerned about sound to/from upstairs than into the adjacent basement space.
I thought perhaps a 3-500cfm in-line remote blower (bathroom exhaust type) would do the trick. It would suck air from a duct high in the interior partition double wall at the theater front and flex snaked down the wall and out the other side bottom into a closet in the adjacent basement space where the fan will be for noise isolation which will discharge the warm theater air into the adjacent basement space out another of the closet walls into the adjacent space. Same scheme at the other end of the theater for intake air (but no blower - this will be how air from the adjacent basement gets in).
Any other thoughts/tricks? Do my heat calcs seem reasonable?
How do others deal with this issue?
db